Piling的PDA test和Working Load Test (WLT) ?
[复制链接] |  
 |  | 
 
| 本帖最后由 kclim_82 于 12-1-2012 11:26 AM 编辑 
 在一场新的工地,当打完所有的piling时候
 
 该如何断定 选择哪个pile来做PDA test和Working Load Test (WLT) ?
 
 RC driven pile, spun pile, bored pile都需要做这2个test 吗?
 
 据我所知, Working Load Test  (WLT) 是放那些stone ( 1.0WL & 2.0WL)然后record settlement & plot graph的,
 
 那么PDA test又是怎样的呢?
 | 
 |  |  |  |
 
|  |  |  
|  |  | 
 |  | 
 
 发表于 13-1-2012 06:18 PM
|
显示全部楼层 |  |  |  |
 
|  |  |  
|  |  | 
 |  | 
 
 发表于 23-1-2012 02:44 PM
|
显示全部楼层 
| 在一场新的工地,当打完所有的piling时候
 该如何断定 选择哪个pile来做PDA test和Working Load Test (WLT) ?
 
 RC driven pile, spun pile, bored pile都需要做这2个test 吗?
 
 据我所知, Working Load Test  (WLT) 是放那些stone ( 1.0WL & 2.0WL)然后record settlement & plot graph的,
 
 那么PDA test又是怎样的呢?
 kclim_82 发表于 12-1-2012 11:23 AM
 
 你所说的wlt应该是mlt,maintain load test,可以分成两种,test on working pile/prelim test pile。working pile通常test to 2x working load,
 prelim test pile就3x working load。
 除了放stone以外也可以用reaction pile来jack那个load.
 
 要做什么test是看consultant定的,要如何选test pile呢?bored pile/driven pile的criteria都不一样的。
 -bored pile-通常都选soil比较差的area/engineer想知道的area。
 -driven pile通常都看bored log才决定,选那些特别的pile来test,比如特别长/特别短的。
 
 PDA=dynamic pile testing,可以check pile的integrity,之后用CAPWAP来estimates total bearing capacity of a pile or shaft, as well as resistance distribution along the shaft and at the toe。
 
 
 除了以上两种,还有pit, sonic logging...
 
 我不是geo的engineer,有错表shoot我
  | 
 |  |  |  |
 
|  |  |  
|  |  | 
 |  | 
 
 
 楼主|
发表于 23-4-2012 05:29 PM
|
显示全部楼层 
| 你所说的wlt应该是mlt,maintain load test,可以分成两种,test on working pile/prelim test pile。w ...y2vlim82 发表于 23-1-2012 02:44 PM
 
 
 会打坏PILE吗?怎么办?IF BROKEN
 | 
 |  |  |  |
 
|  |  |  
|  |  | 
 |  | 
 
 
 楼主|
发表于 4-4-2013 05:41 PM
|
显示全部楼层 |  |  |  |
 
|  |  |  
|  |  | 
 |  | 
 
 发表于 18-6-2013 06:10 PM
|
显示全部楼层 
| working load is it same with ultimate load test? | 
 |  |  |  |
 
|  |  |  
|  |  | 
 |  | 
 
 发表于 8-8-2013 10:18 PM
来自手机
|
显示全部楼层 
| crazy_old_men 发表于 3-6-2013 10:31 AMprelim pile = preliminary pile. 通常在project开始前install来testing用。and is also a non working p ...
Preliminary pile一定会test到damage吗?
 
 还有, 如果Working load pile test到damage了,怎么办?
 | 
 |  |  |  |
 
|  |  |  
|  |  | 
 |  | 
 
 发表于 31-8-2013 08:45 PM
来自手机
|
显示全部楼层 
| crazy_old_men 发表于 12-8-2013 10:59 PMpreliminary test normally will test to 3 times working load.
 
 if working pile test damage means  ...
 Preliminary test pile不会拿来使用???
 | 
 |  |  |  |
 
|  |  |  
|  |  | 
 |  | 
 
 发表于 31-8-2013 11:30 PM
|
显示全部楼层 
| staadpro 发表于 31-8-2013 08:45 PM  Preliminary test pile不会拿来使用???
其实,还是refer回你的project specification...
 
 我做过一场project,specification指明contractor可以propose用preliminary pile 来做 working pile,but subject to SO's approval...
 
 基本上,
 Prelim Pile 是 test on 3x working load
 Working Pile 是 test on 2x working load
 并没有硬性规定Prelim Pile就不可以拿来使用!
 
 
 | 
 |  |  |  |
 
|  |  |  
|  |  |  |  | 